Transformer windings has resistance R1 and R2 in primary and secondary of the transformer. Both resistance and reactance of the windings can be shifted any one side of the two windings using the factor k2. It makes the calculations easy by doing it one side only.
Transformer
windings has resistance R1 and R2 in primary and
secondary of the transformer shown in Figure 1.24. Both resistance and
reactance of the windings can be shifted any one side of the two windings using
the factor k2. It makes the calculations easy by doing it one side
only.
Effective Resistance of Transformer referred to
Primary:
Whenever the
impedance is transferred to primary, it is divided by K2. Then it is
called equivalent secondary resistance and reactance referred to primary and it
is represented as R2' and X2'.
Referred to
Secondary
If primary and
secondary resistance and reactance is transferred to secondary, both resistance
and reactance should be multiplied by k2. R1' and X1'
are the equivalent primary resistance and reactance respectively, referred to
secondary.
Equivalent
Resistance (referred to Secondary)
Primary side
doesn't have any impedance which is shown in above Figure 1.26.
Example 1.11:
A 20 kVA,
2000/200 V, single phase, 50 Hz transformer has a primary resistance of 2.5 Ω
and reactance of 4.8 Ω. The secondary resistance and reactance are 0.01 Ω and
0.018 Ω respectively. Find
(i) Equivalent
reactance referred to primary
(ii) Equivalent
impedance referred to primary
(iii) Equivalent
resistance, reactance and impedance referred to secondary
(iv) Total copper
loss of the transformer.
Solution:
Given data:
(i) Equivalent
resistance referred to primary (R01):
(ii) Equivalent reactance referred to primary (X01):
(iii) Equivalent
resistance referred to secondary (R02):
(iv)Total Copper Losses:
Example 1.12:
A 100 kVA,
1100/200 V single phase transformer has the following parameters R1
= 0.1Ω, X1 = 0.3 Ω, R2 = 0.004 Ω, X2 = 0.012 Ω.
Find equivalent resistance and leakage reactance as referred to high voltage
winding.
Solution
Transformer
rating = 100 kVA,
V1 =
1100 V,
V2 =
200 V
R1 =
0.1 Ω,
X1 =
0.3 Ω,
R2 =
0.04 Ω,
X2 =
0.012 Ω.
Transformation
ratio, k = (V2/V1) = 200/1100 = 0.1818
1100 is the high
voltage side which is primary side.
Equivalent
resistance referred to primary:
Electrical and Instrumentation Engineering: Unit I: Transformer : Tag: : Equivalent Circuit, Solved Example Problems - Shifting Impedance in a Transformer
Electrical and Instrumentation Engineering