Electrical and Instrumentation Engineering: Unit I: Transformer

Shifting Impedance in a Transformer

Equivalent Circuit, Solved Example Problems

Transformer windings has resistance R1 and R2 in primary and secondary of the transformer. Both resistance and reactance of the windings can be shifted any one side of the two windings using the factor k2. It makes the calculations easy by doing it one side only.

SHIFTING IMPEDANCE IN A TRANSFORMER

Transformer windings has resistance R1 and R2 in primary and secondary of the transformer shown in Figure 1.24. Both resistance and reactance of the windings can be shifted any one side of the two windings using the factor k2. It makes the calculations easy by doing it one side only. 


Effective Resistance of Transformer referred to Primary:

Whenever the impedance is transferred to primary, it is divided by K2. Then it is called equivalent secondary resistance and reactance referred to primary and it is represented as R2' and X2'.



Referred to Secondary

If primary and secondary resistance and reactance is transferred to secondary, both resistance and reactance should be multiplied by k2. R1' and X1' are the equivalent primary resistance and reactance respectively, referred to secondary.


Equivalent Resistance (referred to Secondary)


Primary side doesn't have any impedance which is shown in above Figure 1.26.

Example 1.11:

A 20 kVA, 2000/200 V, single phase, 50 Hz transformer has a primary resistance of 2.5 Ω and reactance of 4.8 Ω. The secondary resistance and reactance are 0.01 Ω and 0.018 Ω respectively. Find

(i) Equivalent reactance referred to primary

(ii) Equivalent impedance referred to primary

(iii) Equivalent resistance, reactance and impedance referred to secondary

(iv) Total copper loss of the transformer.

Solution:

Given data:


(i) Equivalent resistance referred to primary (R01):


(ii) Equivalent reactance referred to primary (X01):


(iii) Equivalent resistance referred to secondary (R02):


(iv)Total Copper Losses:


Example 1.12:

A 100 kVA, 1100/200 V single phase transformer has the following parameters R1 = 0.1Ω, X1 = 0.3 Ω, R2 = 0.004 Ω, X2 = 0.012 Ω. Find equivalent resistance and leakage reactance as referred to high voltage winding.

Solution


Transformer rating = 100 kVA,

V1 = 1100 V,

V2 = 200 V

R1 = 0.1 Ω,

X1 = 0.3 Ω,

R2 = 0.04 Ω,

X2 = 0.012 Ω.

Transformation ratio, k = (V2/V1) = 200/1100 = 0.1818

1100 is the high voltage side which is primary side.

Equivalent resistance referred to primary:


Electrical and Instrumentation Engineering: Unit I: Transformer : Tag: : Equivalent Circuit, Solved Example Problems - Shifting Impedance in a Transformer